Level measurement in oil

Status
Not open for further replies.

jdaher

Electrical
Jan 9, 2002
4
0
0
UY
I need to measure the level in a tank with hydrogenated vegetable oil. I have offers with different technologies, radar and ultrasonic. Which technology is more appropriate for this application?

Jorge Fernández Daher
 
Replies continue below

Recommended for you

Jorge:

I've used both. Ultrasonic can't compete with a Radar if you place a value on accuracy, repeatability, nil maintenance, and programmability.

The price of Radar units has also come down quite a bit since its inception and is due to refinements in manufacturing and the number of capable competitors.

I've used Radar on storage tanks, reactors (with internals & agitators), process vessels, and in bridles (external location). I've never had a failure in the operation and with the exception of 2 or 3 installations that had to be re-calibrated (my installation contractor mis-handled), I've had 100% success and satisfaction. This instrument has allowed me to erradicate the need for instrument techs to ever have to enter a process vessel or tank. Confined space entry for these techs has always been a safety risk. I wish I could keep everyone out of having to enter vessels - forever!

I hope this experience helps.

Art Montemayor
Spring, TX
 