Sure, I'll add some information for examples, the protected load is a variable resistive load.I would consider the effect of over-voltage on the loads and set the trips accordingly.
In an area where the utility was known for mistakes, I put an instantaneous overvoltage trip on a set of relays and wired the control circuit of each refrigerant compressor through the relay set.
This was a sausage factory with a lot of refrigeration, for both raw supplies and finished product.
Sure enough, came the day when the utility changed out a transformer bank and fed 416 Volts into a 208 Volt service.
Not one refrigeration system was damaged and no product was lost.
Your voltage relay is not to protect the breaker, it is to protect the load.
You haven't told us anything about the loads.
I want to protect the load from over-voltage and under-voltage when the resistive load changes. I mean, after gradually changing the load, we observe the load voltage and check the relay's behavior in response to these changes.You want to protect the transformer from over-voltage and saturation.
on the transformer secondaryOver-voltage:
In most cases the transformer will be damaged before a resistor bank.
If this is a special application, then set the relay to open the breaker at the maximum allowable voltage.
Under-voltage:
In most cases this is not a concern with a resistor bank.
If this is a special application, then set the relay to open the breaker at the minimum allowable voltage.
Will the relay be on the transformer primary or on the transformer secondary?
Depending on your circuit, you may have to bypass the relay in order to close the breaker.
If you are using this to trip the breaker:on the transformer secondary
you may have to bypass the relay in order to close the breaker.
But the relay here send an information to the breaker to open the circuit,If you are using this to trip the breaker:
Breaker open = no voltage at the relay.What do do you mean by ''bypass it'' ??
Got it, thanks a lotBreaker open = no voltage at the relay.
Depending on the relay the relay may prohibit the closing of the breaker.