I would like some advice about the calculation of a suitable kN value to specify for pull-testing of post-fixed lifting eyes. Some context:
- I am British temporary works engineer who has recently started practicing in Australia
- A 0.5t reinforced concrete Mural is to be lifted by an excavator standing on concrete and then placed on to a pallet for transportation elsewhere by a forklift.
- It will be lifted using 2no post-fixed resin anchors a 2-leg chain using a 20t excavator.
- There will obviously be shear and tension in the anchor during the lift against which I have designed the anchors for and have factored up the load by 1.65 for dynamic effects of using an excavator.
- The client have a calibrated pull-test kit (the type scaffolders use). As it will only test tension and not shear, I have had to specify a pull-test value that will be suitable to confirm the integrity of the installation.
I have settled on the unfactored axial chain load * 1.65 dynamic factor * 1.25 test load and specified this as a pull-test load. Is this an appropriate way to calculate the test load and what do you usually do?
Additionally, I have designed the anchor for a second load case which is the tensile test load as described above to ensure that the integrity of the anchor installation will not be damaged during the test.
I put this into the demo section as it is a demolition contractor doing the work and they are not likely to apply finesse to the installation and lift procedure. Therefore I wanted some demolition engineers take on this situation.
Thanks in advance.
I would like some advice about the calculation of a suitable kN value to specify for pull-testing of post-fixed lifting eyes. Some context:
- I am British temporary works engineer who has recently started practicing in Australia
- A 0.5t reinforced concrete Mural is to be lifted by an excavator standing on concrete and then placed on to a pallet for transportation elsewhere by a forklift.
- It will be lifted using 2no post-fixed resin anchors a 2-leg chain using a 20t excavator.
- There will obviously be shear and tension in the anchor during the lift against which I have designed the anchors for and have factored up the load by 1.65 for dynamic effects of using an excavator.
- The client have a calibrated pull-test kit (the type scaffolders use). As it will only test tension and not shear, I have had to specify a pull-test value that will be suitable to confirm the integrity of the installation.
I have settled on the unfactored axial chain load * 1.65 dynamic factor * 1.25 test load and specified this as a pull-test load. Is this an appropriate way to calculate the test load and what do you usually do?
Additionally, I have designed the anchor for a second load case which is the tensile test load as described above to ensure that the integrity of the anchor installation will not be damaged during the test.
I put this into the demo section as it is a demolition contractor doing the work and they are not likely to apply finesse to the installation and lift procedure. Therefore I wanted some demolition engineers take on this situation.
Thanks in advance.