podobing
Electrical
- Jan 28, 2013
- 49
Hello,
Is this possible:
At one of our customer's mining substations, they operate 2 -10 MVA transformers in parallel. The transformers are 69 kV primary (delta) to 12.47 kV (resistance grounded wye). At some point in time, the center fuse on one of the transformers (T1) blew. The fuse size is 100 E. These stations are rather remote, and it was not known on what day the fuse blew or what the weather was like when it happened.
As the underground mining activity has progressed, this substation is rather lightly loaded, and only supplies power to several underground conveyor belts, so the blown fuse was not realized until a weekly inspection. The plan was to take transformer T1 out of service on the weekend.
Before the weekend arrived, the center fuse on the other transformer (T2) blew. That fuse was replaced and it blew again. Running out of options, they replaced the center fuse on transformer T1, isolated transformer T2, and that is how they are currently running. They want to test and possibly replace T2 during the next planned power outage in a few months.
Both transformers have lightning arresters (MOV type - not porcelain) mounted next to their high voltage bushings. From ground level, the arresters LOOK okay. Is it possible that the center arresters are damaged internally, caused the fuse(s) to blow, but later allowed the power to be re-applied?
Just wandering if anyone has seen anything like this before, or if there is another explanation out there.
Thanks.
Regards,
Dave
Is this possible:
At one of our customer's mining substations, they operate 2 -10 MVA transformers in parallel. The transformers are 69 kV primary (delta) to 12.47 kV (resistance grounded wye). At some point in time, the center fuse on one of the transformers (T1) blew. The fuse size is 100 E. These stations are rather remote, and it was not known on what day the fuse blew or what the weather was like when it happened.
As the underground mining activity has progressed, this substation is rather lightly loaded, and only supplies power to several underground conveyor belts, so the blown fuse was not realized until a weekly inspection. The plan was to take transformer T1 out of service on the weekend.
Before the weekend arrived, the center fuse on the other transformer (T2) blew. That fuse was replaced and it blew again. Running out of options, they replaced the center fuse on transformer T1, isolated transformer T2, and that is how they are currently running. They want to test and possibly replace T2 during the next planned power outage in a few months.
Both transformers have lightning arresters (MOV type - not porcelain) mounted next to their high voltage bushings. From ground level, the arresters LOOK okay. Is it possible that the center arresters are damaged internally, caused the fuse(s) to blow, but later allowed the power to be re-applied?
Just wandering if anyone has seen anything like this before, or if there is another explanation out there.
Thanks.
Regards,
Dave