There's a key issue that has not been addressed here. Is your roof metallic, heavy gauge, and electrically continuous with the structure? If you have a membrane roof material, other non-conductive roof, or flimsy metal roof, expect lightning damage unless you install air terminals. If you have a heavy-gauge metal roof continuous with the steel structure, you should be fine.
The steel columns can be used as down conductors in either case.
You should provide ground rods at grade around the perimeter of the building, bonded to your down conductors, to ensure that the lightning does not dissipate itself through the concrete footings.
----------------------------
The rest of this post applies only to US/NFPA installations:
Get a copy of NFPA 780, it clearly describes all of this.
If you do opt to install a lightning protection system, your consultant's recommendations really have very little to do with it. What concerns you is the UL Master Label that should be provided by your LP system installer. Your consultant has nothing to do with the Master Label. The only real point to having a consultant on an LP system is for coordination with the architectural systems. Any other drawings/specs/advice from your consultant is a worthless waste of money as they will be overridden by the installer, he won't provide the Master Label unless HE is happy with the installation.