Lightning protection of smokestack (IEC)

Status
Not open for further replies.

sparkview

Electrical
Nov 12, 2015
59
Dear all,

There's a new smokestack being constructed, and apparently the developer changed its standard design. The "old" design included that there's dedicated copper wire from the smokestack interception rod to the rod/earthing network. According to the developer, the steel structure is already a conductor and, as such, will conduct any lightning stroke and surge to ground. Below is a drawing of the situation. The picture on the left side shows the "old" design (interception rod with dedicated copper wire to the earthing network), and the picture on the right side shows the proposed "new" design. Are there any changes in IEC-62305 or other relevant standards that might provide some details?

Many thanks in advance for any help.

Kind regards,

Litghning_Protection-Smokestack_p3zk0n.jpg
 
Replies continue below

Recommended for you

According to IEC 62305-3/2006 Para.5.3.5 natural components may be used as down-conductors