I am using the CSA-B72-M87 Installation code for lightning protection systems.
It is closely related to NFPA 780.
My building is a standard industrial facility, with the framework comprising of structural steel that is connected to the ground grid via bolted/welded connections.
According to the CSA standard:
According to NFPA 780:
So my question is this:
If I have air terminals and copper down conductors, do they need to be connected to a grounding rod directly? Or can i simply connect them to the structural steel closest to grade level (at the bottom of the building?)
It is closely related to NFPA 780.
My building is a standard industrial facility, with the framework comprising of structural steel that is connected to the ground grid via bolted/welded connections.
According to the CSA standard:
8.6 Use of Reinforcing Steel
Reinforcing steel in an exterior wall, in a column, or in a reinforced concrete post that complies with CSA Standard CAN3-A23.3, may be used as a down conductor or ring conductor if the electrical continuity of the bars equivalent to No. 2 AWG is ensured.
According to NFPA 780:
4.16 Structural Steel Systems.
4.16.1 General. The structural steel framework of a structure shall be permitted to be utilized as the main conductor of a lightning protection system if it is electrically continuous or is made electrically continuous.
So my question is this:
If I have air terminals and copper down conductors, do they need to be connected to a grounding rod directly? Or can i simply connect them to the structural steel closest to grade level (at the bottom of the building?)