Was reading < with interest.
Has anyone dealt with transformer startup surges & inverter sources?
This installation shall have a 112.5 kva 3ph 480:208/120 transformer at the house, about 1000 ft. away from the utility building (feed).
The utility building shall also house PV-fed grid-tie inverters, and battery-fed backup inverters/generator.
The BU inverters won't be able to source enough current for the transformer's inrush. (The inverter manufacturer stated:
30 Minutes = 6500W
5 Minutes = 7200W
1 minute = 8400W
100 Milliseconds = 150A
(per unit @120V; there will be one/phase.) They don't appear to have any kind of soft-start.
Other people have proposed schemes such as having an oversized generator that starts first, handles the inrush, then shifts the load to the BU inverters, and shuts down again until needed for battery recharge. I'm not enthralled with such, for several reasons.
I spoke to an retired friend who designed & built large [100KW-several MW] UPS's and the transformers within them. (He is the only person I've ever met who really understands both low and high-power transformer magnetics, especially ferromagnetics; vs. reading the textbook, as I did years ago. He holds patents in the area.)
He reminded me the surge is really because you hit the xfmr with voltage at a random point in the cycle, as compared to the residual flux remaining from the point of interruption; if only you knew exactly when and reenergized then, there's almost no bump. (They did this for some of their schemes.)
Custom low-inrush transformers came up, but if I followed his thinking, they have lower efficiency by a significant amount, and far higher price tags; and still may not be low enough for the inverters.
His alternative was to put resistance in series with the inverter output, sized to keep the worst-case current within the inverter ratings, start it, and after the transformer is ...realigned? [not sure what word is best here..]; shunt the resistance out, and then reconnect the loads. This would take milliseconds, but he wouldn't hazard a guess of how many without a lot more data on the transformer in question. (But way below tens of seconds; likely less than a second. His first thought was the pickup time alone of that shunting contactor would be enough, even without an added delay.)
The break in power is acceptable; any scheme I can see that prevents that has offsetting disadvantages. (We can put the non-laptop computers/TV's on small UPS's, etc.)
If possibly viable, I'd propose paying him for a few hours consulting; it would be way less money than any other approach, such as upsizing the inverters.
I welcome comments on this topic.
Has anyone dealt with transformer startup surges & inverter sources?
This installation shall have a 112.5 kva 3ph 480:208/120 transformer at the house, about 1000 ft. away from the utility building (feed).
The utility building shall also house PV-fed grid-tie inverters, and battery-fed backup inverters/generator.
The BU inverters won't be able to source enough current for the transformer's inrush. (The inverter manufacturer stated:
30 Minutes = 6500W
5 Minutes = 7200W
1 minute = 8400W
100 Milliseconds = 150A
(per unit @120V; there will be one/phase.) They don't appear to have any kind of soft-start.
Other people have proposed schemes such as having an oversized generator that starts first, handles the inrush, then shifts the load to the BU inverters, and shuts down again until needed for battery recharge. I'm not enthralled with such, for several reasons.
I spoke to an retired friend who designed & built large [100KW-several MW] UPS's and the transformers within them. (He is the only person I've ever met who really understands both low and high-power transformer magnetics, especially ferromagnetics; vs. reading the textbook, as I did years ago. He holds patents in the area.)
He reminded me the surge is really because you hit the xfmr with voltage at a random point in the cycle, as compared to the residual flux remaining from the point of interruption; if only you knew exactly when and reenergized then, there's almost no bump. (They did this for some of their schemes.)
Custom low-inrush transformers came up, but if I followed his thinking, they have lower efficiency by a significant amount, and far higher price tags; and still may not be low enough for the inverters.
His alternative was to put resistance in series with the inverter output, sized to keep the worst-case current within the inverter ratings, start it, and after the transformer is ...realigned? [not sure what word is best here..]; shunt the resistance out, and then reconnect the loads. This would take milliseconds, but he wouldn't hazard a guess of how many without a lot more data on the transformer in question. (But way below tens of seconds; likely less than a second. His first thought was the pickup time alone of that shunting contactor would be enough, even without an added delay.)
The break in power is acceptable; any scheme I can see that prevents that has offsetting disadvantages. (We can put the non-laptop computers/TV's on small UPS's, etc.)
If possibly viable, I'd propose paying him for a few hours consulting; it would be way less money than any other approach, such as upsizing the inverters.
I welcome comments on this topic.