Anyone have any experience with transmission line impedance calculations using OPGW static wires (ones with fiber optic cable in the center) and how the impedance differs from standard EHS or HSS static wires (steel static wires)?
Just curious, as we've got a debate here over whether our calculations are correct. The ratio of zero-sequence reactance to positive-sequence reactance using a standard EHS or HSS static wire is typically around 3 to 3.5. With the OPGW wires, we're getting ratios of around 2 to 2.5.
I think what we're getting is right, as the OPGW static wires have larger diameters and lower inductive reactances than standard static wires, but wondered if someone could give a sanity check.
Thanks in advance....