- Nov 1, 2018
- 18
I have a wind farm generation & tie-meter design where the meter location is at a wind farm and the point-of delivery for LBA and PPA settlements is several miles down a radial 345kV transmission line (at bus of transco). A few loss compensation questions have come up. Line loss only, no transformer losses need be considered as part of this installation.
1. Does the reactive impedance of the line have any impact on the calculated line losses that will be subtracted from the generation for a loss-compensated energy value (real watts and w-hr)? The argument was made that the settlements are based on 'real' power and only subject to the resistive component of the line impedance. e.g If the phase currents are measured, the per phase real power line losses really should be just I-sq-R (not dependent on X) where I is the magnitude of the phase current, for a line modeled as a series resistance and reactance with no shunt components. And per-phase reactive power line losses should be I-sq-X (not dependent on R). With that said, depending on the line construction and line charging characteristic at different generation levels, does it impact the real losses?
2. If simply a I-sq-R calculation, is it acceptable to average the meter phase currents, such that 3 times Iavg-sq-R represents the total losses. Or, should a per phase loss be calculated and then summed to get a total loss? The later would assume balanced 3-phase generation, which I think would be the case.
3. If this loss calculation was performed outside the meter, at what cycle rate should the loss calc (compensated watts) be done as to ensure an accurate integrated w-hr results (calculated accumulator and/or periodic load profile register data). For example, consider two (2) separate generators sharing the same common line to the point of delivery. This would first require reading uncompensated data from two (2) meters, one (1) for each generator. Then, losses would need to be proportionately calculated and assigned based on the real-time production of each generator. Then compensated data written back into 'compensated' analog and accumulated registers of each meter for separate SCADA and energy accounting processes.
1. Does the reactive impedance of the line have any impact on the calculated line losses that will be subtracted from the generation for a loss-compensated energy value (real watts and w-hr)? The argument was made that the settlements are based on 'real' power and only subject to the resistive component of the line impedance. e.g If the phase currents are measured, the per phase real power line losses really should be just I-sq-R (not dependent on X) where I is the magnitude of the phase current, for a line modeled as a series resistance and reactance with no shunt components. And per-phase reactive power line losses should be I-sq-X (not dependent on R). With that said, depending on the line construction and line charging characteristic at different generation levels, does it impact the real losses?
2. If simply a I-sq-R calculation, is it acceptable to average the meter phase currents, such that 3 times Iavg-sq-R represents the total losses. Or, should a per phase loss be calculated and then summed to get a total loss? The later would assume balanced 3-phase generation, which I think would be the case.
3. If this loss calculation was performed outside the meter, at what cycle rate should the loss calc (compensated watts) be done as to ensure an accurate integrated w-hr results (calculated accumulator and/or periodic load profile register data). For example, consider two (2) separate generators sharing the same common line to the point of delivery. This would first require reading uncompensated data from two (2) meters, one (1) for each generator. Then, losses would need to be proportionately calculated and assigned based on the real-time production of each generator. Then compensated data written back into 'compensated' analog and accumulated registers of each meter for separate SCADA and energy accounting processes.