- Nov 7, 2009
- 384
Hi all,
I would like to obtain your technical opinion on the matter below. I thank you in advance for any clarification response I will get.
In high and low resistance grounded systems, in the event of a ground fault, the unfaulted phase conductors will be subjected a line-ground voltage equal to line-line voltage (especially if the NGR is open-circuited).
However, what about the neutral conductor (NGR to transformer X0? In my opinion, it will remain at system nominal L-N voltage and will not behave the same way as the unfaulted phase conductors.
Anyone agree with me? I only have difficulty justifying this understanding on the neutral conductor and would need some help. NEC 2017 section 250.187.(B).(2) -(Impedance grounded systems), which states that "The neutral conductor shall be insulated for the maximum neutral voltage"...by how much? is also not clear.
Regards,
I would like to obtain your technical opinion on the matter below. I thank you in advance for any clarification response I will get.
In high and low resistance grounded systems, in the event of a ground fault, the unfaulted phase conductors will be subjected a line-ground voltage equal to line-line voltage (especially if the NGR is open-circuited).
However, what about the neutral conductor (NGR to transformer X0? In my opinion, it will remain at system nominal L-N voltage and will not behave the same way as the unfaulted phase conductors.
Anyone agree with me? I only have difficulty justifying this understanding on the neutral conductor and would need some help. NEC 2017 section 250.187.(B).(2) -(Impedance grounded systems), which states that "The neutral conductor shall be insulated for the maximum neutral voltage"...by how much? is also not clear.
Regards,