We are changing chilled water system control strategy from head pressure to DIFFERENTIAL Pressure control between flow and return on the index leg at the most hydraulically remote locations to the VSD Secondary chilled water pumps.
Differential pressure transmitter which was preliminary selected is Siemens QBE3000-D6 with range 0-6bar (0-10V output to suite our QBMS panel)
However, there are concerns about differential pressure transmitter responses in case of negative pressure in supply line which may happen at the start of cycle. (if the cooling load applied to AHUs field cooling coils valves (2-way) will open and (VSD Pumps are off) the head pressure in supply line can be negative)
I have contacted Siemens. The response Siemens gave me “In the situation of negative pressure nothing happens. Mechanically the sensor will be not damaged of course. The electronics are not sealed at the zero point. There is no usable signal available. In the case of 4 ... 20 mA the output can be min 3.7 mA ... 3.8 mA depending on component tolerance. The voltage output will remain at 0 volts”
However, The question still remaining: how differential pressure transmitter will determine differential pressure between flow and return if voltage output will remaining 0 at variations of negative pressure ?
Has anyone had this experience in using Liquid differential pressure responds? Changing closed loop system control to differential pressure control?
Could you please help and confirm in case of negative pressure at “high” port and if the voltage output remain at 0V how differential pressure transmitter will determine differential pressure between flow and return????
Would anyone have by any chance a video of liquid dP responses on your site?
Thanks
Regards
Differential pressure transmitter which was preliminary selected is Siemens QBE3000-D6 with range 0-6bar (0-10V output to suite our QBMS panel)
However, there are concerns about differential pressure transmitter responses in case of negative pressure in supply line which may happen at the start of cycle. (if the cooling load applied to AHUs field cooling coils valves (2-way) will open and (VSD Pumps are off) the head pressure in supply line can be negative)
I have contacted Siemens. The response Siemens gave me “In the situation of negative pressure nothing happens. Mechanically the sensor will be not damaged of course. The electronics are not sealed at the zero point. There is no usable signal available. In the case of 4 ... 20 mA the output can be min 3.7 mA ... 3.8 mA depending on component tolerance. The voltage output will remain at 0 volts”
However, The question still remaining: how differential pressure transmitter will determine differential pressure between flow and return if voltage output will remaining 0 at variations of negative pressure ?
Has anyone had this experience in using Liquid differential pressure responds? Changing closed loop system control to differential pressure control?
Could you please help and confirm in case of negative pressure at “high” port and if the voltage output remain at 0V how differential pressure transmitter will determine differential pressure between flow and return????
Would anyone have by any chance a video of liquid dP responses on your site?
Thanks