Being in the deep south I recently had a couple jobs where the mechanical engineer specified heat tracing for sprinklers under an open canopy.
As far south as I am if the building is unheated but insulated we've never had a problem but a branch line exposed to the outside will eventually freeze and burst.
From a 2010 article
Mr. Isman goes on to say how he doesn't think it is possible to develop a listed heat trace system for branch lines but I suppose anything is eventually possible.
Does anyone know of a system that is listed for branch lines? I bet the answer is no but I got to ask anyway.
As far south as I am if the building is unheated but insulated we've never had a problem but a branch line exposed to the outside will eventually freeze and burst.
From a 2010 article
Ken Isman 2010 said:"Heat Tracing for Fire Sprinkler Systems"
Heat tracing can be used on risers and mains of fire sprinkler systems to prevent the piping from freezing. As of right now, heat tracing cannot be used on branch lines of fire sprinkler systems unless the heat tracing receives a special listing for this use, and we are unaware of any companies that have received this special listing.(Isman 2010)
Mr. Isman goes on to say how he doesn't think it is possible to develop a listed heat trace system for branch lines but I suppose anything is eventually possible.
Does anyone know of a system that is listed for branch lines? I bet the answer is no but I got to ask anyway.