tchnikal
Mechanical
- Jun 21, 2003
- 1
We have 4 Carrier Mod 16JT-150 LiBr/water absorber chillers, 1,500 ton capacity each, using steam at 110psi to the generator. Design is 9.9 lbs of steam per ton. We're experiencing loss of capacity, can only squeeze 65% at full load conditions. It almost appears as though condensate is backing up and not able leave the machine fast enough through the drain heat exchanger float valve. Only two of the four machines have these symptoms. However, condensate from all four absorbers discharge into a common header. The condensate header is not presureizing. I'm inclined to believe the problem is internal to the machine. The steam flow control valve will open 100% to compensate for full load, but the steam flow will not exceed 65% of full flow capacity which would be 15,000 lbs per hour. The steam flow differential across the steam control valve decreases, telling me the flow has decreased. The drain heat exchanger float valves were inspected and checked out OK. We stopped using octal alchohol (wetting agent)because we were told there were side effects. However, the problem existed even before we stopped using it. There is a bypass around the drain heat exchanger float valve, which when opened will increase capacity, but efficiency suffers as a result and it also creates steam impingement on the drain heat exchanger tubes causing them the fail. Would appreciate any input that would help solve our capacity problem.