Live load for fire escape

Status
Not open for further replies.

insajn

Civil/Environmental
Apr 2, 2017
26
The ASCE says it should be 4.79 KN/m[sup]2[/sup] however can this be reduced when the building is only a residential building with 2 apartments per storey ?
 
Replies continue below

Recommended for you

4.79 seems reasonable. The same uniform loads is used on stairs.
 
I don't think that the code allows for reducing this live load. It is set at this level not so much for handling the LL of people fleeing a fire, so much as it is supposed to accommodate the load of the firefighters and the hoses and equipment and such that they might be lugging up the steps. Your location would not minimize that need.
Dave

Thaidavid
 