A question for the structural engineering community: The ASCE/IBC load combinations include a combination under the ASD Basic Load Combinations for D+(W or E)+L+(Lr or S or R). When two or more transient loads are combined in this section a 0.75 factor on the live loads may be used. Now here is the question, how many engineers use this load combination for C&C design of say a rafter or bar joist?
Here is an example that would be typical for my part of the country. Assume a roof snow load of 20 psf (unreducible) and the wind load minimum inward pressure of 10 psf.
S = 20 psf
W = 10 psf
0.75(20 psf + 10 psf) = 22.5 psf > 20 psf for snow
However, I don't know personally of any engineers who would design for 22.5 psf in this case as nobody combines the roof live load with wind.
The typical interpretation I hear is that this load combination is intended for design of elements such as columns where axial load results from the lateral loads.
Do you agree or disagree???