IceNine
Structural
- Feb 24, 2006
- 282
Hello-
I have a mezzanine consisting of steel bar joists spanning 40', spaced at 24" o.c. with a 3 1/2" non composite concrete slab.
My client wants to install a new rack system in which the the legs of the rack fall on every 5th joist or so. My question is, if the legs fall directly over a bar joist, do you think the conc. slab is stiff enought to spread the load such that the adjacent bar joists will share the load? Or should I analyze the one joist directly below for the entire load?
Any comments will be appreciated.
thanks, Ice
I have a mezzanine consisting of steel bar joists spanning 40', spaced at 24" o.c. with a 3 1/2" non composite concrete slab.
My client wants to install a new rack system in which the the legs of the rack fall on every 5th joist or so. My question is, if the legs fall directly over a bar joist, do you think the conc. slab is stiff enought to spread the load such that the adjacent bar joists will share the load? Or should I analyze the one joist directly below for the entire load?
Any comments will be appreciated.
thanks, Ice