SE2607
Structural
- Sep 24, 2010
- 245
If a roof deck will be used by people, ASCE 7 says I need to use the same live load as the occupancy served (table 4.3-1).
Is the Cd = 1.00 or 1.25?
Thank you,
Is the Cd = 1.00 or 1.25?
Thank you,
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Can't you say that about any loading?Honestly, probably zero hours at full design loads
Unless I have a really good reason not to, I follow Table 2.3.2 of the NDS which give CD=1.0 for an Occupancy Live Load.Is the Cd = 1.00 or 1.25?
For occupancy loads - probablyCan't you say that about any loading?
I mean, the lawyers could pull security camera footageThe approach by pham is reasonable but how are you going to know the number of hours of use "at or near design load"?
I guess that is my question. Is it L or Lr?We've always used the duration of load factor (DLF) applicable to each load combination used.
So for your D+L check you'd use 1.0
For a D+Lr check you'd use 1.25
etc. for all the different load combinations - using a DLF based on the basic load case with the highest DLF in each particular combo.
The NDS appendix shows examples of load combinations with appropriate DLF factors for each.
Hopefully you're not confusing load factors with duration of load factors.
For the entire structure all at once, you're probably right. Average live load in a house is only 6psf, after all. But some areas will see it, and that's the point.Honestly, probably zero hours at full design loads
Yes, a deck. A roof deck. No one is going to be living (sleeping) on it. I can't see it being loaded for 7 days.Use CD = 1.0.
A deck? it's going to be more than 7 days.
Well a deck built and put there for the accumulation of people is a deck occupancy for simple live load.I guess that is my question. Is it L or Lr?
This is a roof on a single family residence.Well a deck built and put there for the accumulation of people is a deck occupancy for simple live load.
That would be, in my book, a public assembly function with LL=100 psf.
No snow in Huntington Beach, CA, 2 blocks from the ocean.But the deck also is in essence a "roof" which gets roof live load (Lr=20 psf) and possibly very heavy snow loads (depending on where it's located) where the SL > 100 psf.
Yes, ASD.I would check all applicable load combinations - each combo using a different DLF for the wood's allowable stress (assuming you're using ASD).
You probably would guess that in a low snow load location the LL=100 psf would control.
Ref. ASCE 7 Table 4.3-1:I'd still be tempted to go with 100 psf. Think of the crazy parties that might attract shoulder-to-shoulder people.
At the very least 75 psf.
This is an interesting point. Would a roof deck be considered a deck per ASCE and require 150% live load? I want to say no, but I really don't know.This isn't the question, but I always use a minimum of 60 psf for a deck unless I'm trying to make an existing one work.
Balconies and decks (1.5 x 40 = 60 PSF) are listed separately from roof decks (40 PSF) in table 4.3-1. Intuitively, this makes sense in that it seems less likely that a roof deck, not as accessible as a balcony or patio deck at the same level as a floor, would be overloaded.This is an interesting point. Would a roof deck be considered a deck per ASCE and require 150% live load? I want to say no, but I really don't know.