pajce
Electrical
- Jan 18, 2007
- 40
Hi guys,
how do you model load on the distribution feeder for steady condition Power Load Flow?
program I work with have options:
1. Constant Power load
2. Constant Current load
3. Constant Impedance load.
problem I have is at my company, we are so used to presenting loads (Power Flow Studies) as Constant Power.
Well, when changing the voltage on the TS bus, say increasing by 5%, my current in the model will go down ( due to S=const). Well I humbly don't believe that is the case in the "real life". I would expect current to follow voltage, 5% voltage increase on line will bring increase in current and vice versa. (in steady condition)
Am I right?
If so, what determines type of load for my study?
Thank you for any comment
how do you model load on the distribution feeder for steady condition Power Load Flow?
program I work with have options:
1. Constant Power load
2. Constant Current load
3. Constant Impedance load.
problem I have is at my company, we are so used to presenting loads (Power Flow Studies) as Constant Power.
Well, when changing the voltage on the TS bus, say increasing by 5%, my current in the model will go down ( due to S=const). Well I humbly don't believe that is the case in the "real life". I would expect current to follow voltage, 5% voltage increase on line will bring increase in current and vice versa. (in steady condition)
Am I right?
If so, what determines type of load for my study?
Thank you for any comment