I have a friend that is constructing a grain containment building. The overall size is 37.5ft wide X 72ft long with load-bearing walls constructed of CCA/ACQ lumber as detailed below. A tarp frame kit will be added to the top of the walls to complete the enclosure
The stub walls are 4' high and are constructed of 6x6 #2SYP CCA posts placed on 4' centers (36-40" of post set in concrete below garde, 4' above grade). The posts are lined on the inside with 2x6 T&G #2SYP ACQ planking. Modeling the grain as a fluid, I calculated the force on the 72' walls to be 57,000 lbs distriubted across 18 posts. This would be an average load of 3000 lbs acting perpindicular to the post 1.5' above grade. The load on the 37.5' wall also works out to about 3000lbs per post(30,000lbs across 9 posts). Is this design sufficient, or do we need to add some support cables across the width of the building?
The stub walls are 4' high and are constructed of 6x6 #2SYP CCA posts placed on 4' centers (36-40" of post set in concrete below garde, 4' above grade). The posts are lined on the inside with 2x6 T&G #2SYP ACQ planking. Modeling the grain as a fluid, I calculated the force on the 72' walls to be 57,000 lbs distriubted across 18 posts. This would be an average load of 3000 lbs acting perpindicular to the post 1.5' above grade. The load on the 37.5' wall also works out to about 3000lbs per post(30,000lbs across 9 posts). Is this design sufficient, or do we need to add some support cables across the width of the building?