bafco
Electrical
- Dec 22, 2004
- 9
I have a customer with a Powerflex 40 VFD, 10 HP, driving 5 1.5HP motors. We employed a single MTE load reactor between the VFD and the motors. As long as the system runs on a 4kHz carrier, we don't have a problem. Unfortunately, this customer has found the audible motor noise undesireable, and has increased the carrier to 12kHz. With the given load, that is the maximum carrier allowed according to AB's derating curve. Since this increase in carrier, this customer has smoked 2 reactors. I simulated his conditions in the lab today, and found that at 4kHz, the reactor surface temp was around 180 F. At 12kHz, rose rather quickly to almost 300 F. This customer also almost always runs his motors at 25~30 Hz.
The reactor has the following ratings:
Fundamental Amps - 18
Max Amps - 27
0.8 mH.
Is there a way to predict the required load reactor, while maintaining an equivalent impedance and level of protection as the model currently being used. I think all I need is a reactor that can handle the thermal load and being slammed with a 12kHz carrier, but, I have no idea how to size it. The reactor currently in use has a published carrier limit of 20kHz, but the melted terminal block begs to differ.
The reactor has the following ratings:
Fundamental Amps - 18
Max Amps - 27
0.8 mH.
Is there a way to predict the required load reactor, while maintaining an equivalent impedance and level of protection as the model currently being used. I think all I need is a reactor that can handle the thermal load and being slammed with a 12kHz carrier, but, I have no idea how to size it. The reactor currently in use has a published carrier limit of 20kHz, but the melted terminal block begs to differ.