I'm working on a load study for a "data center".
Basically, the task is to determine if an existing power distribution system is capable of handling some additions to the server racks.
I know from years of experience how difficult it is to calculate electrical loads for computer/server type rack mounted equipment based on nameplate load info. The client is pushing for an entire upgrade for the UPS, generator, etc.. that feeds the server room (about 1k sq ft rack room). Does anyone know of any good standards to follow for designing/justifying power available per sq. ft. for such type of rooms?
Quick internet searches today show that such rooms are designed anywhere from 50 W/ft^2 to 400W/ft^2. My "gut" (a.k.a. experience) tells me that the existing power system is perfectly capable of carrying addition loads in racks. In my experience... computer/server/network type equipment generally operates at about 10% of its nameplate input power. But I need a standard to follow to show the client this... The client is not satisfied with simply field "measuring" the existing demand load, then working from there...
Any advice? Or any IEEE standards out ther that can help me out justifying W/ft^2 for server type rooms?
Thanks!
If it were "my" data center, I would not even hesitate to say: "the existing power systems is just fine.... plug it up!!!". But I need a standard to follow to show the client this...
Basically, the task is to determine if an existing power distribution system is capable of handling some additions to the server racks.
I know from years of experience how difficult it is to calculate electrical loads for computer/server type rack mounted equipment based on nameplate load info. The client is pushing for an entire upgrade for the UPS, generator, etc.. that feeds the server room (about 1k sq ft rack room). Does anyone know of any good standards to follow for designing/justifying power available per sq. ft. for such type of rooms?
Quick internet searches today show that such rooms are designed anywhere from 50 W/ft^2 to 400W/ft^2. My "gut" (a.k.a. experience) tells me that the existing power system is perfectly capable of carrying addition loads in racks. In my experience... computer/server/network type equipment generally operates at about 10% of its nameplate input power. But I need a standard to follow to show the client this... The client is not satisfied with simply field "measuring" the existing demand load, then working from there...
Any advice? Or any IEEE standards out ther that can help me out justifying W/ft^2 for server type rooms?
Thanks!
If it were "my" data center, I would not even hesitate to say: "the existing power systems is just fine.... plug it up!!!". But I need a standard to follow to show the client this...