ThePunisher
Electrical
- Nov 7, 2009
- 384
HI all, I understand that when cable sizing (in our case, based on CEC) is being used, the cables are sized based on 125% of rated load current. In our case, it is a 15 kV VFD power cable, 350 MCM, with published manufacturer ampacity of 435A and the indoor ambient temperature of 30 deg C, the ampacity remains 435 A.
The motor drawn continuous current was originally 317A. Hence the cable was originally 73% loaded (lower than 80%) or the cable ampacity is 137%.
The motor operating point changed which required it to draw 380A. Now the cable is already loaded to 380/435 = 87.4%. Technically it should be ok but do I need CEC variance as I already exceeded 80% loading? Since, this is medium voltage application, the supply equipment and protection should have the capability to be 100% load rated.
Your comments is appreciated.
The motor drawn continuous current was originally 317A. Hence the cable was originally 73% loaded (lower than 80%) or the cable ampacity is 137%.
The motor operating point changed which required it to draw 380A. Now the cable is already loaded to 380/435 = 87.4%. Technically it should be ok but do I need CEC variance as I already exceeded 80% loading? Since, this is medium voltage application, the supply equipment and protection should have the capability to be 100% load rated.
Your comments is appreciated.