Good day!!!
We have been using 3-phase, 3-wdg power transformers connected YG-YG-D, with voltage ratings of 115/34.5/13.8 kV and capacity of 83MVA...Our standard now is to use the tertiary winding only as a stabilizing winding, with one point of the delta grounded...
However, we are planning to utilize the tertiary wdg now to serve the station transformer, normally connected D-YG...
Does anybody have any experience on this? what must be the proper connections to avoid operational problems such as ferroresonance or whatever? should one point of the delta of both the station XF and tertiary of the main XF be grounded or not? or should we leave the grounded point of the delta tertiary grounded and then have the tertiary of the station xf ungrounded?
the station XF shall be connected thru UG power cables with approx 20m from the tertiary of the main XF.
Another scenario that I'm looking into is the possiblity of using an open delta pole mounted transformers as station XF instead of the 3P padmounted, which would significantly reduce the cost. Any comment on this?
We have been using 3-phase, 3-wdg power transformers connected YG-YG-D, with voltage ratings of 115/34.5/13.8 kV and capacity of 83MVA...Our standard now is to use the tertiary winding only as a stabilizing winding, with one point of the delta grounded...
However, we are planning to utilize the tertiary wdg now to serve the station transformer, normally connected D-YG...
Does anybody have any experience on this? what must be the proper connections to avoid operational problems such as ferroresonance or whatever? should one point of the delta of both the station XF and tertiary of the main XF be grounded or not? or should we leave the grounded point of the delta tertiary grounded and then have the tertiary of the station xf ungrounded?
the station XF shall be connected thru UG power cables with approx 20m from the tertiary of the main XF.
Another scenario that I'm looking into is the possiblity of using an open delta pole mounted transformers as station XF instead of the 3P padmounted, which would significantly reduce the cost. Any comment on this?