Takket3
Mechanical
- Apr 28, 2016
- 21
Hi… question…….
I’m looking to locate a differential pressure sensor for a secondary pump VFD in a chilled water system. The chilled water system serves process equipment and runs 365 days a year.
I know that typically you want the sensor across your most remote piece of equipment to make sure you have enough DP to move water though the control valve, coil, etc. In this case my most remote unit is one that only uses chilled water in the summer. In the winter time this unit’s chilled water valve is closed.
Father upstream there are other units the serve a process and use chilled water all year long.
I know in the summertime I’ll be fine but in the winter time, when my remote AHU chilled water valve is closed, and my process equipment still wants chilled water, will I run into problems? I would think I’ll be okay because the pressure in my supply and return headers is still going to fluctuate at my remote AHU even if its chilled water valve is closed, right?
Basically my question is, is it okay to leave the sensor at my remote AHU or should I locate it farther upstream before the unit that uses chilled water all year?
And also, at the "remote AHU" there are taps off the main header with shutoff valves. Is it okay to put the sensor after the shutoff valves instead of in the main header? If I do this I only have to drain the piping to the remote AHU instead of the whole header to make the pipe tap. The pressure should more or less be the same in each place, right?
I’m looking to locate a differential pressure sensor for a secondary pump VFD in a chilled water system. The chilled water system serves process equipment and runs 365 days a year.
I know that typically you want the sensor across your most remote piece of equipment to make sure you have enough DP to move water though the control valve, coil, etc. In this case my most remote unit is one that only uses chilled water in the summer. In the winter time this unit’s chilled water valve is closed.
Father upstream there are other units the serve a process and use chilled water all year long.
I know in the summertime I’ll be fine but in the winter time, when my remote AHU chilled water valve is closed, and my process equipment still wants chilled water, will I run into problems? I would think I’ll be okay because the pressure in my supply and return headers is still going to fluctuate at my remote AHU even if its chilled water valve is closed, right?
Basically my question is, is it okay to leave the sensor at my remote AHU or should I locate it farther upstream before the unit that uses chilled water all year?
And also, at the "remote AHU" there are taps off the main header with shutoff valves. Is it okay to put the sensor after the shutoff valves instead of in the main header? If I do this I only have to drain the piping to the remote AHU instead of the whole header to make the pipe tap. The pressure should more or less be the same in each place, right?