Location of Hangers on mains

Status
Not open for further replies.

eatapeach

Military
Jun 20, 2013
76
I can't find anywhere in the NFPA 13 that addresses the hanger locations at bends or change in directions. Are supports not required within a certain distance of a change of direction? All I see in NFPA 13 for 4" steel pipe is every 15'. I am in a seismic category B so 9.4 doesn't apply. I also was searching for a maximum length allowed for 3/8" threaded rod supporting steel pipe. I have seen stiffeners on threaded rod before but I cant find where its called out to be of a certain length before installing them. Can anyone help with these two questions.
Thanks
 
Replies continue below

Recommended for you

Seismic bracing is required at changes in direction. There is nothing about hangers being required at a change in direction. You just have to adhere to the distances, but there shall be a hanger on each section of pipe or between branch lines.

There is nothing I can see about the maximum length of 3/8" rod.