The terms "Locked Rotor Current" and "Full Load Amps" and particularly "Locked Rotor Current" are mostly used in connection with squirrel cage induction motors and synchronous motors.
In the case of torque motors locked rotor amps and FLA are often equal.
A wound rotor motor may be configured as a torque motor with lots of rotor resistance. In this case, the locked rotor amps may be less than rated full load amps. Of course the motor will not produce full load power with that much rotor resistance.
Actually, without supplementary cooling, the locked rotor amps will be a lot less than rated full load amps.