eemotor
Electrical
- Sep 26, 2003
- 51
Hello to all,
I've been going through NEMA and IEEE standards trying to conclude the generally accepted minimum stall time for a 4000V, 3ph., 60HZ, 1250HP induction motor. NEMA specifies that that motors should be able to withstand locked rotor currents for at least 12 seconds. However, this only applies to motors rated at 500HP or less. IEEE 112-1996 specifies that the readings for the locked rotor test should be taken within 5 seconds after voltage is applied. Does anyone know of a standard or specification that might indicate the locked rotor time otherwise. Thank you all.
I've been going through NEMA and IEEE standards trying to conclude the generally accepted minimum stall time for a 4000V, 3ph., 60HZ, 1250HP induction motor. NEMA specifies that that motors should be able to withstand locked rotor currents for at least 12 seconds. However, this only applies to motors rated at 500HP or less. IEEE 112-1996 specifies that the readings for the locked rotor test should be taken within 5 seconds after voltage is applied. Does anyone know of a standard or specification that might indicate the locked rotor time otherwise. Thank you all.