mbk2k3
Electrical
- Nov 18, 2010
- 97
hey folks,
i have a 2000ft cable that feeds a 4.16kV switchgear lineup. the cable has a 1200A breaker at the source end, so it will protect the cable adequately.
my question is this: does my 4.16kV switchgear lineup require a protection device on the line side (breaker/fuse)? are there any references to NEC/CEC that may provide a guideline?
client is suggesting using a load break switch only.
the reason i ask is because i figure the 1200A breaker will do an adequate job of protecting the cable, but what if there is a fault at the switchgear. wouldn't you want a fuse/breaker on the line side of the switchgear to quickly clear any faults and prevent damage to the cable?