It is intended to run protection CT secondary leads a distance of 1300 meters to a back-up earth fault relay.
The CT is installed on a transformer neutral with a 250A Neutral Earth Resistor.
CT ratio = 250 : 1
CT class = 5VA Class 5 P10 ( to IEC 185 )
CT class = 5P 50 F10 ( to AS 1675 )
Relay = Alstom type MCSU, In = 1A
Relay burden at max setting of 0.152A = 0.0007 VA
Therefore relay impedance at max setting = 0.0007 / 0.152^2 = 0.03 Ohm.
Impedance of CT secondary lead loop = 21 Ohm.
The 5VA CT could push the relay set current of 0.152A through an impedance of R = 5 / 0.152^2 = 216 Ohm.
Therefore the CT can deliver the set current of 0.152A through the burden impedance of 21.03 Ohm.
Question:
What other considerations are necessary for this installation ?
The CT is installed on a transformer neutral with a 250A Neutral Earth Resistor.
CT ratio = 250 : 1
CT class = 5VA Class 5 P10 ( to IEC 185 )
CT class = 5P 50 F10 ( to AS 1675 )
Relay = Alstom type MCSU, In = 1A
Relay burden at max setting of 0.152A = 0.0007 VA
Therefore relay impedance at max setting = 0.0007 / 0.152^2 = 0.03 Ohm.
Impedance of CT secondary lead loop = 21 Ohm.
The 5VA CT could push the relay set current of 0.152A through an impedance of R = 5 / 0.152^2 = 216 Ohm.
Therefore the CT can deliver the set current of 0.152A through the burden impedance of 21.03 Ohm.
Question:
What other considerations are necessary for this installation ?