Someone brought me a truss design to look over the other day. One of our salesmen sent it in to the office for review.
I know that some of you probably know this stuff better than I do. But others may not deal with trusses a lot. There are new engineers every year. And not everyone who reads the thread is an engineer. So if you feel like I'm talking down to you or telling you things you already know, it's not intended to offend anyone.
Here's the basic truss:
I know you can't see a lot of detail. The span is 77'. It's 3' 6" tall at the low end and about 5' tall at the high end. Spaced 2' OC with 30-10-10 loading.
A few things jump out at me right away. Looks like it meets the deflection criteria:
L/240 for live load and L/180 for total load are allowable in this area. So what's the actual deflection?
The live load and dead load together total well over 4".
So what kind of ceiling does the building have? The salesman doesn't know.
Are there interior walls? Don't know.
Is an architect or engineer involved? No, this is apparently someone winging it on their own. (Not at all uncommon in this area)
With L/180 allowed for total load, the truss easily slid by the design program. Total deflection could have had up to a little more than 5".
What else comes to mind?
Wind loading for end verticals is something you have to turn on for every truss. It got missed on this design.
So does my train of thought have a caboose?
There are 2 things I want to emphasize. I think there ought to be max deflection limits that are numbers rather than L/ numbers on long span trusses. L/180 is fine for a 28' residential truss. But in a situation like this it's not.
If any of you are involved in similar projects I'd suggest specifying max deflection as a number.
This truss should be deeper. The guy probably thought a shallower truss would be cheaper. But that's not the case in situations like this.
Another very serious issue I have with this truss is erection bracing. Trusses like these have a tremendous amount of force in the chords just with their own weight. With the TC in compression it will want to buckle awfully badly. Without a ridiculous amount of bracing it will be difficult to keep them upright until the plywood is applied.
I did a job with trusses similar to the one above a few years back. When I sent in the sealed drawings I sent a letter along with them stating my concern about erection bracing. They assured me they knew what they were doing.
Here's the result:
I know that some of you probably know this stuff better than I do. But others may not deal with trusses a lot. There are new engineers every year. And not everyone who reads the thread is an engineer. So if you feel like I'm talking down to you or telling you things you already know, it's not intended to offend anyone.
Here's the basic truss:
I know you can't see a lot of detail. The span is 77'. It's 3' 6" tall at the low end and about 5' tall at the high end. Spaced 2' OC with 30-10-10 loading.
A few things jump out at me right away. Looks like it meets the deflection criteria:
L/240 for live load and L/180 for total load are allowable in this area. So what's the actual deflection?
The live load and dead load together total well over 4".
So what kind of ceiling does the building have? The salesman doesn't know.
Are there interior walls? Don't know.
Is an architect or engineer involved? No, this is apparently someone winging it on their own. (Not at all uncommon in this area)
With L/180 allowed for total load, the truss easily slid by the design program. Total deflection could have had up to a little more than 5".
What else comes to mind?
Wind loading for end verticals is something you have to turn on for every truss. It got missed on this design.
So does my train of thought have a caboose?
There are 2 things I want to emphasize. I think there ought to be max deflection limits that are numbers rather than L/ numbers on long span trusses. L/180 is fine for a 28' residential truss. But in a situation like this it's not.
If any of you are involved in similar projects I'd suggest specifying max deflection as a number.
This truss should be deeper. The guy probably thought a shallower truss would be cheaper. But that's not the case in situations like this.
Another very serious issue I have with this truss is erection bracing. Trusses like these have a tremendous amount of force in the chords just with their own weight. With the TC in compression it will want to buckle awfully badly. Without a ridiculous amount of bracing it will be difficult to keep them upright until the plywood is applied.
I did a job with trusses similar to the one above a few years back. When I sent in the sealed drawings I sent a letter along with them stating my concern about erection bracing. They assured me they knew what they were doing.
Here's the result: