Loop feed 43.8 kV pad mounted oil filled transformer

Status
Not open for further replies.

pgbengr

Electrical
Mar 9, 2007
4
I need help from any engineer who has experience working with 43.8 kV power distribution system in Alabama in terminating 46 kV class loop feeder cables to a padmount tranformer. Can you list tranformer and switchgear manufacturers or furnish a link?
Thanks. PGBENGR.
 
Replies continue below

Recommended for you

I've never heard of a distribution system over 34.5 kV. IEEE/ANSI standards for pad-mounted transformers cover 34.5 kV and below.
 
Alabama Power Company supplies electric power to a customer at 43.8 KV- subtransmission Voltage.
 
Square D literature indicate they can supply pad mount transformers up to 43.8kV.

Alan
“The engineer's first problem in any design situation is to discover what the problem really is.” Unk.
 