Logan82
Structural
- May 5, 2021
- 212
Hi,
I have a mandate in which there is an industrial bridge for a gantry crane. The bridge is over 100 years old. The bridge is seldom used, so fatigue is not an issue. The bridge is built of A7 Steel with a low fracture toughness resistance (Charpy V-Notch Test Result: 8 J at 0°C). There is no beam redundancy in this bridge (only 2 main beams). The main beams are almost used at 100 % in flexion (so there is significant tension at the bottom of these beams).
Some engineers in this mandate argue that this bridge can be used above 0°C, saying that this test is necessary only when the beams are subjected to temperature under 0°C. However, I can't find anything backing this claim.
Are there some arguments that could justify using this structure above 0°C? So far, I am leaning toward recommending a replacement of the main beams.
Thank you in advance!
I have a mandate in which there is an industrial bridge for a gantry crane. The bridge is over 100 years old. The bridge is seldom used, so fatigue is not an issue. The bridge is built of A7 Steel with a low fracture toughness resistance (Charpy V-Notch Test Result: 8 J at 0°C). There is no beam redundancy in this bridge (only 2 main beams). The main beams are almost used at 100 % in flexion (so there is significant tension at the bottom of these beams).
Some engineers in this mandate argue that this bridge can be used above 0°C, saying that this test is necessary only when the beams are subjected to temperature under 0°C. However, I can't find anything backing this claim.
Are there some arguments that could justify using this structure above 0°C? So far, I am leaning toward recommending a replacement of the main beams.
Thank you in advance!