- 44
We have a 12" slab on grade and some small amount of foundation work (say, 18 yd3), which had a low f'c (around 2800 psi). Corrected core tests from over 56 days came in at around 3550, which is more than the spec'd f'c = 3500.
Petrographic tests/micrographs show the culprits to be very high entrained air (10 - 15% and locally higher), and a w/c ratio of 0.55, when 0.45 max was spec'd. Entrained air is spec'd at 6%(should have been 3% max for fdtn/interior).
Delamination is a possible issue. The slabs are now covered with vinyl comp tile. I'm thinking of recommending:
1. checking for delamination with a hammer/chain drag test
2. accepting the concrete (based on strength considerations)
3. fining the contractor heavily
The alternative is to require all the work to be redone.