I recently came across a very interesting problem.
We have a motor with the following characteristics.
- 75 HP TEFC
- 900 RPM
- 460V
- Nameplate amps @ 460V - 111amps, with 1.15 SF
- In. Class - F
- Efficiency - 94.5%
- Power Factor - .68
This motor is paired to a VFD that is a typical 75HP VFD rated for 96 amps, per the NEC design criteria. The VFD is a typical Yaskawa Z1000 with an Arteche type KS harmonic filter and a soft start bypass.
When we operate the motor and VFD we are getting a current draw of 120 amps. The VFDs were then upgraded to 100 HP drives so that they can handle the excessive current being generated by the motors.
My question is
- When you have a motor with such a low power factor, how is recommended to size a VFD? I assume we should simply oversize the drive. Would that be correct or is there something else that needs to be done with the VFD in order to make it work with the motor?
We have burned up 1 VFD and 1 motor thus far and I am wondering if anyone has any insight on how to deal with this. I am considering replacing the motors as i have found similar motors that should work that woudl get us within the NEC current drwa guidelines.
If any more information is needed please let me know and thanks in advance for any help.
Rob
I recently came across a very interesting problem.
We have a motor with the following characteristics.
- 75 HP TEFC
- 900 RPM
- 460V
- Nameplate amps @ 460V - 111amps, with 1.15 SF
- In. Class - F
- Efficiency - 94.5%
- Power Factor - .68
This motor is paired to a VFD that is a typical 75HP VFD rated for 96 amps, per the NEC design criteria. The VFD is a typical Yaskawa Z1000 with an Arteche type KS harmonic filter and a soft start bypass.
When we operate the motor and VFD we are getting a current draw of 120 amps. The VFDs were then upgraded to 100 HP drives so that they can handle the excessive current being generated by the motors.
My question is
- When you have a motor with such a low power factor, how is recommended to size a VFD? I assume we should simply oversize the drive. Would that be correct or is there something else that needs to be done with the VFD in order to make it work with the motor?
We have burned up 1 VFD and 1 motor thus far and I am wondering if anyone has any insight on how to deal with this. I am considering replacing the motors as i have found similar motors that should work that woudl get us within the NEC current drwa guidelines.
If any more information is needed please let me know and thanks in advance for any help.