Per NEC, it is required for transformer secondary conductors less than 1000V that are over 100 feet long without an OCPD on the secondary of the transformer and that do not have differential protection. It is also required for conductors over 1000V.
As dpc says it's easiest if you're using software that shows this automatically. If not, you might want to check the withstand capability in situations where:
-The available short circuit current is high,
-The trip time is long (e.g. no instantaneous trip),
-The amount of conductor cross section is low, which may be caused by:
--Taking advantage of higher insulation temperature ratings,
--Taking advantage of a low ambient temperature and applying a derating factor, and
--Using an installation method that allows higher amapacities (e.g. free air ratings)
You may also want to check your grounded conductor in very large installations with parallel conductors where you're at the bottom of Table 250.102(C)(1). You may also want to check in cases where you're using relays with LVPCBs instead of integral trip units.