Upstream:
Breaker: ICCB
Rating: 800AF/400AT
Rating Plug (In): 400A (1.0 P.U)
Long time trip setting, magnitude (Ir), Adjustable: 300A (0.75 P.U)
Long time trip setting, time (tr): there are many bands. The TCC mentions trip time for all the bands at 1.5 times the pickup setting.
Downstream:
Breaker: MCCB
Rating: 250AF/250AT
Rating Plug (In): 250A
Long time trip setting, magnitude (Ir), Not Adjustable: As per the curve
Long time trip setting, time (tr): Not Adjustable: As per the curve
When I check the TCC of downstream MCCB at 1.5 times the pickup value, it trips between 90~200s
The TCC of upstream ICCB at 1.5 times the pickup value, for the band C9, the trip time is between 119~224s
Asking this, if this would cause any other problem just doing a manual check? Have attached the TCC curves of upstream and downstream
Breaker: ICCB
Rating: 800AF/400AT
Rating Plug (In): 400A (1.0 P.U)
Long time trip setting, magnitude (Ir), Adjustable: 300A (0.75 P.U)
Long time trip setting, time (tr): there are many bands. The TCC mentions trip time for all the bands at 1.5 times the pickup setting.
Downstream:
Breaker: MCCB
Rating: 250AF/250AT
Rating Plug (In): 250A
Long time trip setting, magnitude (Ir), Not Adjustable: As per the curve
Long time trip setting, time (tr): Not Adjustable: As per the curve
When I check the TCC of downstream MCCB at 1.5 times the pickup value, it trips between 90~200s
The TCC of upstream ICCB at 1.5 times the pickup value, for the band C9, the trip time is between 119~224s
Asking this, if this would cause any other problem just doing a manual check? Have attached the TCC curves of upstream and downstream