I am using SKM to perform a power system analysis (short circuit,coordination, and arc flash). When performing he arc flash calculations through the software per IEEE 1584, the table summary gives me the bus bolted fault current, bus arcing fault current, protective device bolted fault current, and protective device arcing fault current.
1. Why would the bolted fault current at the bus be different than the bolted fault current at the protective device?
2. Why is the arcing fault current at the bus different than the bus arcing fault current?
Based on my studies, IEEE 1584 calculates the bus arcing fault current based on several factors (including gap distance between conductors, whether arc is in a box or open air, etc.). Where can I find information that discusses how this derived value is further reduced to come up with the protective device arcing fault current?
As always, I appreciate you taking the time to read and comment.
DJR
1. Why would the bolted fault current at the bus be different than the bolted fault current at the protective device?
2. Why is the arcing fault current at the bus different than the bus arcing fault current?
Based on my studies, IEEE 1584 calculates the bus arcing fault current based on several factors (including gap distance between conductors, whether arc is in a box or open air, etc.). Where can I find information that discusses how this derived value is further reduced to come up with the protective device arcing fault current?
As always, I appreciate you taking the time to read and comment.
DJR