Sirs,
Could you please confirm the lower limit of 220kV three phase line loading?
For steady state stability delta should be between 30 and 45 degrees, and
so steady power transfer can be P = 220*220*sin37.5/(400) ie nearly 60.5 MW
to 85 MW. (SIL=120).