I wonder if there are much to mention about the required lug contact area for grounding conductors into steel structures and down conductors to lightning protection systems.
10 times the copper required cross-section area seems like a rule of thumb for some utilities when using steel structures as part of the grounding system especially for CT and VT structures. Nothing is mentioned about the lugs tho.
In IEC world however, the IEC 62271-301 dimensioning the equipment terminals suggests a current density of about 0.33 A/sq.mm for copper joints, that can be a basis to get a lug area?
Any clues?
10 times the copper required cross-section area seems like a rule of thumb for some utilities when using steel structures as part of the grounding system especially for CT and VT structures. Nothing is mentioned about the lugs tho.
In IEC world however, the IEC 62271-301 dimensioning the equipment terminals suggests a current density of about 0.33 A/sq.mm for copper joints, that can be a basis to get a lug area?
Any clues?