Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

LV Cable Selection - Voltage Rating - Single Phase, 700V rms 1

Status
Not open for further replies.

Instrument1352

Electrical
Apr 9, 2014
28
Hi,
I have an application where the supply is a "float" 700V rms, 50hz and the load is 50m away about 5kw, all at ambient temperature.
Normal power cables are rated 0.6/1kv which seem to be ok (0.6kv core-earth and 1kv core-core), however my concern is if a fault occurs and one of the cores is short to earth, then it would exceed the insulation rating of 0.6kv core-earth.
What exact cable would you suggest for this application?
Thank you!
 
Replies continue below

Recommended for you

It looks like,
1)you are from IEC world
2)your 700V system is high resistance grounded

Based on above you have to select the cable designated as 1.8/3.0(3.3)kV.
To my knowledge there is no cable available between 0.6/1kV & 1.8/3.0(3.3)kV in the IEC/ BS world.
 
Hi Kiribanda,
Having to use MV cable was my fear. Makes everything more difficult, from engineering, to procurement & installation and a whole lot of other head aches.
Probably I need to face my fate!
 
IEC allows use of 600V/1000V cables for unearthed system as well, provided the protection scheme ensures automatic detection and isolation of earth faults in <1 min. There is some hope.
 
I am sorry, but I think IEC 60502-1/2004 recommends as maximum voltage Uo [line-to-ground] only 0.6 kV for 0.6/1.2 kV. For 0.7>0.6 it has to be 1.8/3 kV rated.
IEC_60502-1_b2jfvv.jpg
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor