LV CABLES WORKING AT -30C

Status
Not open for further replies.

Elecme

Electrical
Apr 24, 2002
46
What is the effect on both the copper and insulation of a low voltage copper cable when working at ambient temperature of -30C.are there any special consideration for the type of cable to be used;I mean special insulation type. Elecme
 
Replies continue below

Recommended for you

At those loer temperatures tha insulation will get stiff. Your "plastic" insulations such as PVC and PE will stiffen up on you quite a bit. If you don't have to handle them or move them at these low temperatures, you shouldn't have any problems. Crews in Wyoming during the winter either want to wait for a warmer day to install the cables or keep them inside until the last minute to pull them in. The stiifness can increase the pulling tensions when pulling into a conduit system.

If you're worried about the flexiblity, try to find an equivalent cable with EPR insulation. It'll be a lot more flexible at those lower temperatures, but that added flexibility will come at a price.

As for the effects on copper, it'll be plenty happy at those temperatures.

Mark in Utah
 
I agree with Mark, and only want to add that XLPE is generally available in -40 as well.
 