- Jun 21, 2007
- 99
Can somebody help me in selection of LV contactor (starter) for Transformer switching?
NEMA ICS 2 Table 2-4-17 gives the max kVA ratings for Transformers with 1 to 20 times of Inrush current.
Now for a 600V, single phase application, max. kVA rating is given as 135kVA.
However, for us , we have a 150kVA Transformer which is Oil filled.
I suspect that the inrush current will not be as high as 20times.
Now the question : If I can get the exact inrush current value, can I select a Contactor which may be lower in size compared to what NEMA ICS 2 prescribes?