Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

LVL sloped hanger

Status
Not open for further replies.

JStructsteel

Structural
Aug 22, 2002
1,331
0
36
US
Have a LVL for a stair stringer, sloped obviously. 2 ply, so 3.5" wide. What Simpson hanger do you suggest, I was looking at the HUCQ, but they dont make that in a sloped configuration.
Any other suggestions, or suggestions to connect to the perimeter beam?
Thanks
 
Replies continue below

Recommended for you

JStructsteel,

Assuming that the beam is at the lower end of the stringer, I've used both sloped seat connectors like the LSSR as well as flat seat ones with the bottom of the stringer cut flat to match the width of the seat. As long as you don't overcut, I wouldn't really consider this a notch, since the "notched" portion of the member is fully supported.

FWIW, my preferred detail for a stringer to beam connection at the lower end is to rest the stringer directly top of the beam. Of course, this isn't always possible.
 
Status
Not open for further replies.
Back
Top