MAWPeter
Chemical
- Aug 6, 2023
- 1
Typically my relief valve set pressure is set at my MAWP, but I have a case where my set pressure is below MAWP because of a small, but constant back pressure.
If my vessel is rated for 45 psig, but my set pressure is 42.5 psig, what is my MAAP for a fire scenario? If I'm telling a relief valve vendor my set pressure and using 21% overpressure for fire, I would expect my MAAP would be limited by the valve at 51.4 psig. Thoughts?
If my vessel is rated for 45 psig, but my set pressure is 42.5 psig, what is my MAAP for a fire scenario? If I'm telling a relief valve vendor my set pressure and using 21% overpressure for fire, I would expect my MAAP would be limited by the valve at 51.4 psig. Thoughts?