Section80
Chemical
- Sep 17, 2018
- 1
Hi, always thanks to your precious advice
I'd like to ask for your advice and knowledge for Steam PSV design. Currently I review Steam generation system and the relief pressure is around 120 barg and relief flow is around 100 t/h.
PSV discharge is sized to 6" x 28" in order to meet the mach number.
1) Our stress team oppose current design due to stress problem orignated from big discharge line and request to reduce the discharge line size. So when I reduce PSV discharge size to 24", the mach number becomes 0.89. Normally the PSV discharge mach number shall not over 0.7, but some of my colleague said Mach number under 1 is allowable if it relieve it to the ATM.
Is there anyone who have seen these criteria in specific code? I reference API 520/521 but there are no specific comment for mach number that relieve to the ATM case.
2) Some other colleague said that if the mach number is over than 0.7, noise will be the other issue for this design. In this case, is it OK to install acoustic insulation only?
It would be appreciate to advice for above issue. Thank you for reading.
I'd like to ask for your advice and knowledge for Steam PSV design. Currently I review Steam generation system and the relief pressure is around 120 barg and relief flow is around 100 t/h.
PSV discharge is sized to 6" x 28" in order to meet the mach number.
1) Our stress team oppose current design due to stress problem orignated from big discharge line and request to reduce the discharge line size. So when I reduce PSV discharge size to 24", the mach number becomes 0.89. Normally the PSV discharge mach number shall not over 0.7, but some of my colleague said Mach number under 1 is allowable if it relieve it to the ATM.
Is there anyone who have seen these criteria in specific code? I reference API 520/521 but there are no specific comment for mach number that relieve to the ATM case.
2) Some other colleague said that if the mach number is over than 0.7, noise will be the other issue for this design. In this case, is it OK to install acoustic insulation only?
It would be appreciate to advice for above issue. Thank you for reading.