MartinLe
Civil/Environmental
- Oct 12, 2012
- 394
I'm dealing with a sub contractor who points out that MID flowmeters are not suitable for heating circuits with added glycol, because of the magnetite.
My understanding is that magnetite forms at high temperature and high pH.
This is a cooling circuit, highest temp. will be 90°C most of the times 75°C at the hottest palce in the circuit.
pH of glycol is in the range of 7,5 - 9
Pipes are black steel (1.0254).
Water will be decarbonated before filling circuit.
My question:
Should I be concerned about magnetite interfering with the MID?
p.s.: The sales engineer for the flowmeters strongly discouraged MID and argued for ultrasonic flow meters, as for now I'll go with this.
My understanding is that magnetite forms at high temperature and high pH.
This is a cooling circuit, highest temp. will be 90°C most of the times 75°C at the hottest palce in the circuit.
pH of glycol is in the range of 7,5 - 9
Pipes are black steel (1.0254).
Water will be decarbonated before filling circuit.
My question:
Should I be concerned about magnetite interfering with the MID?
p.s.: The sales engineer for the flowmeters strongly discouraged MID and argued for ultrasonic flow meters, as for now I'll go with this.