nightfox1925
Electrical
- Apr 3, 2006
- 567
I am having a strange case here. Ona 480VAC system, the arrangement goes like this. There is an MCC with the following feeders: 2 motor loads rated for 3kW, and the rest are transformer feeders rated not greater than 45kVA. The total connected load is 433A and this MCC is connected to an ATS connected to normal and emergency supplies with main breakers rated 400A each. Assuming the ATS is at emergency supply, when the normal comes back, the ATS re-transfers in an open transition scheme. At this point, the 400A main breaker according to the report fails (not trip). In their report, the breaker is damaged and claimed that the 400A breaker is having a rating of 3200A and the in-rush is 11000A (quite strange). I told them to deactivate the instantaneous setting of the main breaker and check settings to allow for in-rush to dissipate. However, they claim that the breaker fails to trip and get damaged. For all I know, there is no such thing as a 3.2kAIC breakerat 480V at 400A. What do you think is the problem? I feel estranged by the way they made the report.