burnt2x
Electrical
- Oct 10, 2007
- 525
Hello!
I have a ground fault protection problem that involves two different directional ground relays and two different PT's (potential trafos wired broken-delta as reference voltage sources). The feeder PT voltage rating is 190 volts and the main breaker PT 110 volts.
We have experienced ground faults during which the main breaker directional ground relay always trips instead of the feeder directional ground relay on faults of the feeder! We have tested the trip times of both relays and found the trip times are graded 200 ms apart for the same ground fault current (i.e. feeder ground fault relay set to trip earlier than the main breaker ground fault relay for the same groudn fault level)
My Q1 is:
Since we have ruled out the relay trip time settings/ grading as the culprit (by testing), is this a problem with reference voltage settings? (one relay with a 110 volt reference source and the other with 190 volt reference) Did I miss something here?
Q2:
The 110-V broken-delta connects with the main braker's 67N ground protection relay with 10% (11 volts) setting while the 190-V broken-delta connects to the feeder directional ground relay with 15 volts setting (around 8% of 190 V), are the voltage reference settings above (10% vs. 8%) correct?
The system is a substation, 4160 volts, ungrounded system.
Any recommendation is accepted.
thank you.
I have a ground fault protection problem that involves two different directional ground relays and two different PT's (potential trafos wired broken-delta as reference voltage sources). The feeder PT voltage rating is 190 volts and the main breaker PT 110 volts.
We have experienced ground faults during which the main breaker directional ground relay always trips instead of the feeder directional ground relay on faults of the feeder! We have tested the trip times of both relays and found the trip times are graded 200 ms apart for the same ground fault current (i.e. feeder ground fault relay set to trip earlier than the main breaker ground fault relay for the same groudn fault level)
My Q1 is:
Since we have ruled out the relay trip time settings/ grading as the culprit (by testing), is this a problem with reference voltage settings? (one relay with a 110 volt reference source and the other with 190 volt reference) Did I miss something here?
Q2:
The 110-V broken-delta connects with the main braker's 67N ground protection relay with 10% (11 volts) setting while the 190-V broken-delta connects to the feeder directional ground relay with 15 volts setting (around 8% of 190 V), are the voltage reference settings above (10% vs. 8%) correct?
The system is a substation, 4160 volts, ungrounded system.
Any recommendation is accepted.
thank you.