I just as well throw this one out there:
I have a facility set up with a 300 kva 3-phase delta 480 system. We have a 400 amp molded-case breaker at the service entrance. It is the normal input to an automatic transfer switch. The emergency feed to the transfer switch is 225 kw diesel generator. The load side of the ATS feeds an MCC with the plant lighting loads and a few motors, the largest of which is an air compressor drive at 50 horsepower.
Here's the problem. We lose the utility frequently. The generator starts up and the ATS trasfers load to the generator without problem. Then, when the utility comes back up, the ATS trasfers the load back to the utility, and the 400-amp breaker trips about half the time.
We have no faults. The circuit breaker has been tested and found serviceable.
The transfer switch is fast. I'm thinking that when the transfer switch operates, the 50-hp motor starts to spin down and presents a reverse and out of phase voltage to the incoming utility breaker. We've been unable to get the breaker to trip on retransfer with that 50-hp motor shut down, but I would really like to nail this problem down. I'm leaning towards a time delay relay to keep that motor offline for a few seconds after voltage loss.
And I'd appreciate your thoughts, ideas, commentary, wisdom, etc.
old field guy
I have a facility set up with a 300 kva 3-phase delta 480 system. We have a 400 amp molded-case breaker at the service entrance. It is the normal input to an automatic transfer switch. The emergency feed to the transfer switch is 225 kw diesel generator. The load side of the ATS feeds an MCC with the plant lighting loads and a few motors, the largest of which is an air compressor drive at 50 horsepower.
Here's the problem. We lose the utility frequently. The generator starts up and the ATS trasfers load to the generator without problem. Then, when the utility comes back up, the ATS trasfers the load back to the utility, and the 400-amp breaker trips about half the time.
We have no faults. The circuit breaker has been tested and found serviceable.
The transfer switch is fast. I'm thinking that when the transfer switch operates, the 50-hp motor starts to spin down and presents a reverse and out of phase voltage to the incoming utility breaker. We've been unable to get the breaker to trip on retransfer with that 50-hp motor shut down, but I would really like to nail this problem down. I'm leaning towards a time delay relay to keep that motor offline for a few seconds after voltage loss.
And I'd appreciate your thoughts, ideas, commentary, wisdom, etc.
old field guy